Why with module FM350-1 does the internal gate STS_GATE remain open in single count mode although the software gate SW_GATE closes?
Description
When using the counter module FM350-1, with the parameters given below, it might happen that although the software gate SW_GATE closes, the internal gate STS_GATE remains open and for this reason the counter group shows no function. The following parameterization leads to this behavior:
* Single count mode
* Counting range 0 to 32 bits
* Gate function failure
* Load value 0
As soon this parameterization sets the software gate SW_GATE to FALSE, counting is interrupted. If the software gate SW_GATE is set to TRUE again, the load value 0 is loaded. This makes the counter module FM350-1 recognize the counting range limit of 0 and counting stops, the STS_GATE remains FALSE and counter value remains 0.
You must change one of the following settings to remedy this behavior.
* Select periodic counting instead of single count mode
* Select a counting range of -31bits to +31bits instead of 0 to 32 bits
* Select a load value not equal to 0
Chịu khó đọc tiếng anh nhé. Chúc bạn thành công
-