    Hi bạn,
    Trong tài liệu biến tần nó ghi lỗi này có thể là những nguyên nhân sau:
    The intermediate circuit voltage is higher then the over voltage limit of the drive. The VLT® will trip with an alarm after a short warning message.
    1. Generating operation:
    a) The down ramps are too short
    b) The inertia of the load is too big
    c) The brake electronics of the VLT® is defective or overloaded
    2. Mains transients in the supply voltage
    3. Over voltage in the power supply
    4. Interaction between the VLT® and the idle current compensation device
    Cách khắc phục là:
    1. Reduce the generative energy:
    a) Set longer down ramps
    b) Reduce the load, activate Over Voltage Control (Par. 2-17) resp. AC Brake (Par. 2-10) (see Note) or use a VLT® with a brake resistor
    c) Please contact your local Danfoss supplier*
    2. Check the mains for possible transients*
    3. Check the mains for possible over voltage
    4. Check mains conditions eventually use idle current compensation devices with chokes